Re: Electrical wiring - routing in a concrete house built in the 70s

Quote:
View Post
I think they will be put in due to the kitchen renovation. I have this line in the works:

Einbau von 3 x FI/LS 13A ( Für GWM)

not sure what FI/LS stands for in German (or GWM for that matter - dishwasher?)
FI/LS in normal language means that the switch will turn of if there is a difference between the main and neutral meaning electric is leaking to somewhere else, could be you, could be a drop of water in your coffee machine causing this.

GWM = Geschirrwaschmaschine = Dishwasher.

You might want to ask what the costs would be to replace your whole cabinet for a modern one where everything has proper RCD protection, and 2 or 3 spare groups for future plans. Your current switches are reaching a certain age where replacement really doesn't harm anyway. And have a main switch for the whole cabinet in it also, those are very handsome when doing work on the cabinet and are not so costly.
Reply With Quote
The following 3 users would like to thank for this useful post:
  #22  
Old 12.02.2020, 15:40
Jdr Jdr is offline
Junior Member
 
Join Date: Feb 2016
Location: Koblenz AG
Posts: 68
Groaned at 0 Times in 0 Posts
Thanked 80 Times in 43 Posts
Jdr is considered knowledgeableJdr is considered knowledgeableJdr is considered knowledgeable
Re: Electrical wiring - routing in a concrete house built in the 70s

Quote:
View Post
I survived without them in the UK for 32 years & Switzerland for a further 20 years, my mother is still alive at 90 & has never had one.

And not that long ago, in CH, I believe in Biel, 2 kids died because the landlord was to cheap to invest 100 CHF in a RCD.......
Classic case of hairdryer-in-bathtub.....


You very seldom need them RCDs, but when you do, you really do.
Reply With Quote
  #23  
Old 12.02.2020, 15:42
fatmanfilms's Avatar
Forum Legend
 
Join Date: Apr 2010
Location: Verbier
Posts: 17,995
Groaned at 324 Times in 260 Posts
Thanked 17,343 Times in 9,472 Posts
fatmanfilms has a reputation beyond reputefatmanfilms has a reputation beyond reputefatmanfilms has a reputation beyond reputefatmanfilms has a reputation beyond reputefatmanfilms has a reputation beyond reputefatmanfilms has a reputation beyond repute
Re: Electrical wiring - routing in a concrete house built in the 70s

Quote:
View Post
Classic case of hairdryer-in-bathtub.....
Darwinian theory in action, people used to be taught to treat electricity with respect.
Reply With Quote
  #24  
Old 12.02.2020, 15:42
Newbie
 
Join Date: Feb 2020
Location: Geneva
Posts: 1
Groaned at 0 Times in 0 Posts
Thanked 0 Times in 0 Posts
ACHIEVEIT has no particular reputation at present
Re: Electrical wiring - routing in a concrete house built in the 70s

Quote:
View Post
1. they are access points - makes it easier to replace a wire if one gets burnt out / eaten / a new spur needed
Without wanting to derail the thread - is it possible to install a power socket in place of the access point? The cables and the hole are already there - the question is, is there usually enough space to make room for the extra space required for the socket? Thanks
Reply With Quote
  #25  
Old 12.02.2020, 15:45
Guest
 
Posts: n/a
Re: Electrical wiring - routing in a concrete house built in the 70s

Quote:
View Post
I survived without them in the UK for 32 years & Switzerland for a further 20 years, my mother is still alive at 90 & has never had one.

Working in the film business we often had 64 amp & 128 amp 3 phase, never had a RCB connected.

Plenty of people will cut the earth connection as they can be a pain in the arse tripping too often, I think that is more dangerous. Sound men on film sets always cut the earth on their extension leads because of hum
RCD's don't need an earth connection to switch of when electricity is leaking through your body

If they trip to often than people should start cleaning their equipement.
Reply With Quote
  #26  
Old 12.02.2020, 15:46
Guest
 
Posts: n/a
Re: Electrical wiring - routing in a concrete house built in the 70s

Quote:
View Post
Darwinian theory in action, people used to be taught to treat electricity with respect.
Nothing to do with respect if you touch your laundry-machine and can't let go anymore while your heart is rushing overtime waiting to collapse.
Reply With Quote
  #27  
Old 12.02.2020, 15:50
fatmanfilms's Avatar
Forum Legend
 
Join Date: Apr 2010
Location: Verbier
Posts: 17,995
Groaned at 324 Times in 260 Posts
Thanked 17,343 Times in 9,472 Posts
fatmanfilms has a reputation beyond reputefatmanfilms has a reputation beyond reputefatmanfilms has a reputation beyond reputefatmanfilms has a reputation beyond reputefatmanfilms has a reputation beyond reputefatmanfilms has a reputation beyond repute
Re: Electrical wiring - routing in a concrete house built in the 70s

Quote:
Nothing to do with respect if you touch your laundry-machine and can't let go anymore while your heart is rushing overtime waiting to collapse.
People should be taught to touch electrical appliance with the back of their fingers first, then if it's live your fingers will contract & break the connection. I was taught this on my first day working in the film business.
Reply With Quote
This user would like to thank fatmanfilms for this useful post:
  #28  
Old 12.02.2020, 15:53
Tom1234's Avatar
Forum Legend
 
Join Date: Jan 2007
Location: Kanton Luzern
Posts: 14,758
Groaned at 466 Times in 372 Posts
Thanked 20,669 Times in 8,564 Posts
Tom1234 has a reputation beyond reputeTom1234 has a reputation beyond reputeTom1234 has a reputation beyond reputeTom1234 has a reputation beyond reputeTom1234 has a reputation beyond reputeTom1234 has a reputation beyond repute
Re: Electrical wiring - routing in a concrete house built in the 70s

Quote:

You might want to ask what the costs would be to replace your whole cabinet for a modern one where everything has proper RCD protection, and 2 or 3 spare groups for future plans. Your current switches are reaching a certain age where replacement really doesn't harm anyway. And have a main switch for the whole cabinet in it also, those are very handsome when doing work on the cabinet and are not so costly.
I'd like to know this too.

Half of our circuits have RCDs and half have just the old screw-in fuses.

Guess which of the two feeds the bathroom?
Reply With Quote
This user would like to thank Tom1234 for this useful post:
  #29  
Old 12.02.2020, 16:03
Phil_MCR's Avatar
Forum Legend
 
Join Date: Oct 2009
Location: Basel
Posts: 13,630
Groaned at 269 Times in 175 Posts
Thanked 16,537 Times in 7,030 Posts
Phil_MCR has a reputation beyond reputePhil_MCR has a reputation beyond reputePhil_MCR has a reputation beyond reputePhil_MCR has a reputation beyond reputePhil_MCR has a reputation beyond reputePhil_MCR has a reputation beyond repute
Re: Electrical wiring - routing in a concrete house built in the 70s

Quote:
FI/LS in normal language means that the switch will turn of if there is a difference between the main and neutral meaning electric is leaking to somewhere else, could be you, could be a drop of water in your coffee machine causing this.

GWM = Geschirrwaschmaschine = Dishwasher.

You might want to ask what the costs would be to replace your whole cabinet for a modern one where everything has proper RCD protection, and 2 or 3 spare groups for future plans. Your current switches are reaching a certain age where replacement really doesn't harm anyway. And have a main switch for the whole cabinet in it also, those are very handsome when doing work on the cabinet and are not so costly.
I guess FI/LS somehow refers to the RCD. I just wondered if anyone know what the letters stand for?
Reply With Quote
  #30  
Old 12.02.2020, 16:04
John_H's Avatar
Forum Legend
 
Join Date: May 2013
Location: Up above Nyon
Posts: 3,570
Groaned at 99 Times in 61 Posts
Thanked 4,553 Times in 1,800 Posts
John_H has a reputation beyond reputeJohn_H has a reputation beyond reputeJohn_H has a reputation beyond reputeJohn_H has a reputation beyond reputeJohn_H has a reputation beyond reputeJohn_H has a reputation beyond repute
Re: Electrical wiring - routing in a concrete house built in the 70s

Quote:
Nothing to do with respect if you touch your laundry-machine and can't let go anymore while your heart is rushing overtime waiting to collapse.
I was an electrician a long time ago. Back before health and safety was really a big thing. Lost count of the amount of shocks I got, thrown off my feet, whole body clenched, falling off ladders after touching live stuff. It kinda became routine and almost funny, attaching meggers to things, giving people shocks etc.

Until one day a guy died, he walked into a bare cable hanging from the ceiling, it wasn't even connected but according to the investigation, it had built up a huge static charge, MICC cable, couple hundred meters long.
Reply With Quote
This user would like to thank John_H for this useful post:
  #31  
Old 12.02.2020, 16:16
Tom1234's Avatar
Forum Legend
 
Join Date: Jan 2007
Location: Kanton Luzern
Posts: 14,758
Groaned at 466 Times in 372 Posts
Thanked 20,669 Times in 8,564 Posts
Tom1234 has a reputation beyond reputeTom1234 has a reputation beyond reputeTom1234 has a reputation beyond reputeTom1234 has a reputation beyond reputeTom1234 has a reputation beyond reputeTom1234 has a reputation beyond repute
Re: Electrical wiring - routing in a concrete house built in the 70s

Quote:
View Post
I guess FI/LS somehow refers to the RCD. I just wondered if anyone know what the letters stand for?
FI: Fehlerstromschutzschalter

(This is your RCD).

LS: Leitungsschutzschalter

(This is your circuit breaker)

So, on this context, LS is basically your electronic over-current fuse and a device with FI/LS also is a residual current device.
Reply With Quote
The following 3 users would like to thank Tom1234 for this useful post:
  #32  
Old 12.02.2020, 16:23
Phil_MCR's Avatar
Forum Legend
 
Join Date: Oct 2009
Location: Basel
Posts: 13,630
Groaned at 269 Times in 175 Posts
Thanked 16,537 Times in 7,030 Posts
Phil_MCR has a reputation beyond reputePhil_MCR has a reputation beyond reputePhil_MCR has a reputation beyond reputePhil_MCR has a reputation beyond reputePhil_MCR has a reputation beyond reputePhil_MCR has a reputation beyond repute
Re: Electrical wiring - routing in a concrete house built in the 70s

Quote:
View Post
FI: Fehlerstromschutzschalter
Thanks. Now someone explain to me how you get FI from Fehlerstromschutzschalter???
Reply With Quote
  #33  
Old 12.02.2020, 16:41
Guest
 
Posts: n/a
Re: Electrical wiring - routing in a concrete house built in the 70s

Quote:
View Post
I was an electrician a long time ago. Back before health and safety was really a big thing. Lost count of the amount of shocks I got, thrown off my feet, whole body clenched, falling off ladders after touching live stuff. It kinda became routine and almost funny, attaching meggers to things, giving people shocks etc.

Until one day a guy died, he walked into a bare cable hanging from the ceiling, it wasn't even connected but according to the investigation, it had built up a huge static charge, MICC cable, couple hundred meters long.
Electrician since mid 80's and same here. Till I in the 90's got stuck for some seconds between 2 different 25A phases. According to people on the same floor I screamed like a pig that got killed, lost control of my Blatter so wet my pants and it took some hours before my heart was back to normal rhythm. Just was lucky the main flow did not pass my heart else it be the end of it. After that I got deep respect, and only once more got a big bang on my hands due to a guy from another technical company who simply removed my warning signs and put the fuse back in while I was working on it. Chased him through half the factory but got to beat him up, after which he complained..., his boss gave him another punch and instantly fired him.

I've had it with "just touch it and you'll know.."
Reply With Quote
The following 3 users would like to thank for this useful post:
  #34  
Old 12.02.2020, 16:44
Guest
 
Posts: n/a
Re: Electrical wiring - routing in a concrete house built in the 70s

Quote:
View Post
Thanks. Now someone explain to me how you get FI from Fehlerstromschutzschalter???
The truth is that some of us work with terms of which we after half a decade still have no clue how they ever thought of it...

Best I can come up with is FehlerEinrichting, and since FE already was taking by earthing they just took the next letter and came up with FI to avoid confusion.
Reply With Quote
The following 2 users would like to thank for this useful post:
  #35  
Old 12.02.2020, 16:47
Tom1234's Avatar
Forum Legend
 
Join Date: Jan 2007
Location: Kanton Luzern
Posts: 14,758
Groaned at 466 Times in 372 Posts
Thanked 20,669 Times in 8,564 Posts
Tom1234 has a reputation beyond reputeTom1234 has a reputation beyond reputeTom1234 has a reputation beyond reputeTom1234 has a reputation beyond reputeTom1234 has a reputation beyond reputeTom1234 has a reputation beyond repute
Re: Electrical wiring - routing in a concrete house built in the 70s

Quote:
View Post
Thanks. Now someone explain to me how you get FI from Fehlerstromschutzschalter???
I had to google this but the I is the symbol for current (same as English).
So loosely translated FI is current error.
Reply With Quote
This user would like to thank Tom1234 for this useful post:
  #36  
Old 12.02.2020, 16:53
bigblue2's Avatar
Forum Legend
 
Join Date: Mar 2009
Location: Glarus
Posts: 8,086
Groaned at 486 Times in 405 Posts
Thanked 14,715 Times in 5,780 Posts
bigblue2 has a reputation beyond reputebigblue2 has a reputation beyond reputebigblue2 has a reputation beyond reputebigblue2 has a reputation beyond reputebigblue2 has a reputation beyond reputebigblue2 has a reputation beyond repute
Re: Electrical wiring - routing in a concrete house built in the 70s

Quote:
View Post
People should be taught to touch electrical appliance with the back of their fingers first, then if it's live your fingers will contract & break the connection. I was taught this on my first day working in the film business.
what about things like washing machines etc that suddenly develop faults? <cough> whirlpool <cough> should you touch everything with the back of your hand? how about pipes and radiators too? You can never have enough electrical safety, people are pretty blasé about electricity now a days, and thats fine, until the one time its not
Reply With Quote
  #37  
Old 12.02.2020, 16:59
Tom1234's Avatar
Forum Legend
 
Join Date: Jan 2007
Location: Kanton Luzern
Posts: 14,758
Groaned at 466 Times in 372 Posts
Thanked 20,669 Times in 8,564 Posts
Tom1234 has a reputation beyond reputeTom1234 has a reputation beyond reputeTom1234 has a reputation beyond reputeTom1234 has a reputation beyond reputeTom1234 has a reputation beyond reputeTom1234 has a reputation beyond repute
Re: Electrical wiring - routing in a concrete house built in the 70s

The worse you can do is touch live with one hand and earth with the other.

Even when working on non-live house circuits , I try and keep one hand away.
Reply With Quote
This user would like to thank Tom1234 for this useful post:
  #38  
Old 12.02.2020, 17:13
fatmanfilms's Avatar
Forum Legend
 
Join Date: Apr 2010
Location: Verbier
Posts: 17,995
Groaned at 324 Times in 260 Posts
Thanked 17,343 Times in 9,472 Posts
fatmanfilms has a reputation beyond reputefatmanfilms has a reputation beyond reputefatmanfilms has a reputation beyond reputefatmanfilms has a reputation beyond reputefatmanfilms has a reputation beyond reputefatmanfilms has a reputation beyond repute
Re: Electrical wiring - routing in a concrete house built in the 70s

Quote:
View Post
what about things like washing machines etc that suddenly develop faults? <cough> whirlpool <cough> should you touch everything with the back of your hand? how about pipes and radiators too? You can never have enough electrical safety, people are pretty blasé about electricity now a days, and thats fine, until the one time its not
In addition to some fault that would make the case live, the earth needs to be broken. Pipes should be earthed, if not likely you will get a tingle in the bath when you touch a tap, this was common in Hotels in France in the 70's unless you have modern plastic piping
Reply With Quote
  #39  
Old 12.02.2020, 21:38
Junior Member
 
Join Date: Oct 2018
Location: Orbe
Posts: 49
Groaned at 1 Time in 1 Post
Thanked 27 Times in 17 Posts
brunobriner has no particular reputation at present
Re: Electrical wiring - routing in a concrete house built in the 70s

Quote:
View Post
Without wanting to derail the thread - is it possible to install a power socket in place of the access point? The cables and the hole are already there - the question is, is there usually enough space to make room for the extra space required for the socket? Thanks
In my apartment these "access points" are bigger than a normal 86x86 so in my case I cannot put a socket, a switch, etc. instead of the cover, therefore I recommend you to remove the cover and check it for yourself if they are the same size as a normal one to start with.
Reply With Quote
  #40  
Old 12.02.2020, 21:44
st2lemans's Avatar
Forum Legend
 
Join Date: Dec 2010
Location: Lugano
Posts: 28,558
Groaned at 1,934 Times in 1,465 Posts
Thanked 33,744 Times in 16,098 Posts
st2lemans has a reputation beyond reputest2lemans has a reputation beyond reputest2lemans has a reputation beyond reputest2lemans has a reputation beyond reputest2lemans has a reputation beyond reputest2lemans has a reputation beyond repute
Re: Electrical wiring - routing in a concrete house built in the 70s

Quote:
View Post
Be aware also that Swiss electricians seem to have a general disdain for the wiring regs - don't expect any wire to necessarily be what it should be according to the sheath colour.
Yes, last year we had the electrical inspection, and several sockets were wired backwards, etc. (never touched since the building was built).

I fixed most myself, so cut the electricians estimate in half.

Tom
Reply With Quote
This user would like to thank st2lemans for this useful post:
Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
renovating a house built in the 50s maloriediana Housing in general 16 30.10.2017 22:16
Re-wiring of house - costs? Castro Housing in general 37 08.03.2017 09:35
"electrical" question [wiring light fixtures] jakobo Housing in general 59 30.03.2011 10:03